Using BACnet Multistate points within Continuum
  • Using BACnet Multistate points within Continuum
  • Dave_Shore
    Dave_Shore
  • Alan_Wood
    Alan_Wood
‎2018-09-06 01:47 PM
Continuum
BACnet
Can't use Multistate points values to trigger graphics or other objects
A third Party Multistate BACnet object needs to be mapped to a Continuum Infinity Numeric before it can be read as number.
A third Party Multistate BACnet object may be read as State 1, State 2, state 3 or On, Off, -On or other values
These should be either mapped to Infinity Strings or Numerical to be displayed or measures as required.
eg.
ContinuumNum = BACnetFullPath\PointName (if a number is required)
Then a ContinuumString can be set based on the ContinuumNum value if the text read from the third party point requires modifying.
Other MultiState Bacnet Notes
When setting the value of a third party Multistate Bacnet Objects eg "Heat", "Cool", "Auto", "Off", try using an integer
ie WriteProperty(Bacnet Object, 4, 1) rather than WriteProperty(Bacnet Object, Heat, 1)
Note: Some 3rd party bacnet devices default their multi-state values to 0 instead of 1. Cyberstation will not accept a default value of 0. Get the 3rd party vendor to set the default to 1 if possible.