Some modbus device documentation indicate that there are 6 digits in a register to obtain certain information
Continuum
Xdriver
Modbus
The Modbus xdriver only allows for 5 digits
The modbus range is from 0-65535, so 6 digits is too large
Some PLCs used the 40,000 and 30,000 notation which embeds the function code in the address.
For example:
30,001= function code 4 start address 0
30,234= function code 4 start address 233
40,001= function code 3 start address 0