Upgrading an Automation Server results in an empty database

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading an Automation Server results in an empty database
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2516 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading an Automation Server results in an empty database

Picard Product_Support
‎2018-09-10 05:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:52 PM

Issue

Upgrading an AS results in an empty database.

Product Line

EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation 1.0.0.173 to 1.1.0.264
  • StruxureWare Building Operation 1.1.0.362 to 1.2.0.767 

Cause

When upgrading the database, the Enterprise Server (ES) upgrades without error, but when upgrading the AS, the result is an empty database.

Resolution

StruxureWare Building Operation 1.0.0.173 to 1.1.0.264
The problem is caused by the initial engineering of the system being carried out on an old AS that was not LON or BACnet specific, copying into new hardware at R1.0 then when upgraded to R1.1 the upgrade fails due to the wrong type of AS being used (LON or BACnet). This practice is not common place and rather rare.

When the trace log is examined, they find that the upgrade fails due to the fact that an illegal object type is attempted to be created – a BACnet interface. This is not legal in an AS-L. The reason that this occurs is that the backup file is from an AS-L that had been restored from a 1.0 AS-B backup file.

Check New Release or Upgrade StruxureWare Building Operation Site Software. The issue you face could possibly be a procedural one and this article clearly defines the steps.

StruxureWare Building Operation 1.1.0.362 to 1.2.0.767
The solution is identifying problems with a period, space, or other character in names. Placing a period at the end of a name or accidentally having a space at the end is suggesting something is following or further action. If using BACnet, please see the note below. Problems with bindings which were still in tact when values were removed also are a potential issue and not properly removed. 
 

Work Around:

  1. Backup AS
  2. Upgrade PC to 1.2
  3. Open Device Administrator
  4. Upgrade AS to 1.2
  5. DO NOT close Device Administrator
  6. Open StruxureWare Workstation
  7. Log into AS
  8. If Database is Blank go back to Web Browser
  9. Connect to AS
  10. Log in
  11. In the top right hand corner of the screen select Setting>Device Configuration
  12. Select the Server Log tab
  13. Click “Get all log files”
  14. Once downloaded, open “trace” using Notepad
  15. Click Edit>Find
  16. Type the word “nsp.csc.UpgradeManager ERROR:”
  17. The error lines run from date stamp to date stamp so isolate the line beginning with the year and ending with the next instance of the year. Here is an example:

    2012-08-29 16:39:32.990 [32] nsp.csc.UpgradeManager ERROR:    Error Parsing Dump Objects:  RecoverableException: source/Path.cppy) ) Error: Invalid_Path (0x10001), module Coml(11), moduleCode 0, dispString "Heatsink Temp.", techString "Path& Path::Append(const UTF8String& name)" 

  18. The “dispString “_______”” section of this line will give you the object name that contains an illegal character.
  19. Downgrade the AS back to 1.1
  20. Locate the dispString object and change the name so that it does not contain any illegal characters. This is typically a name ending in a period. NOTE: when the rename dialogue pops up, it will indicate that an illegal character is present to confirm you are modifying the right object.
  21. Backup the AS
  22. Re-Upgrade the AS to 1.2
  23. If the upgrade fails, repeat steps 9-20 or call product support. Be prepared to provide a Db backup at 1.1 as well as the trace file from the 1.2 failed upgrade.

BACnet Note: A BACnet device including an object name "East Duct Max." is no longer valid because of the illegal character at the end of the name. Before upgrading the ES from 1.1 to 1.2, remove any full stops/periods from any object names. "East Duct Max." is changed to "East Duct Max"  Other illegal characters include *°?|/"<> or ~ and an object cannot begin or end with a white space or period. Select TPA-SBO-12-0008.00 - ES upgraded from 1.1 to 1.2 loses database to review this TPA.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 18548
  • 6469
  • defect
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of