Upgrading DPU 7910 and 7920 Rev Levels
  • Upgrading DPU 7910 and 7920 Rev Levels
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:53 PM
Issue with DPUs after an upgrade to the system.
If you have upgraded and changed out the EPROMs on the board, but it does not seem to be getting any Transactions or Time Schedules to work properly.
I/NET site with Access Control
Upgrading DPU controllers
  1. Connect to the controller, select Edit/ Host Computer/Network Configuration
  2. Penetrate the Link Summary, Penetrate the Controller, penetrate the DPUs
  3. At this point the rev level will be different, do not modify it to put the correct rev level.
  4. Instead leave it blank and the software will fill it in automatically.
  • TAC INET
  • 2814