Updating the UPD Files for MR-AHUs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Updating the UPD Files for MR-AHUs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1364 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Updating the UPD Files for MR-AHUs

Picard Product_Support
‎2018-09-06 03:09 PM

Issue

Updating the UPD Files for MR-AHUs

Environment

I/NET Seven Site

Cause

How to download a different application to an MR-AHU in order to control the economizer damper 

Resolution

There are times when the user needs to download a different application to an MR-AHU in order to control the economizer damper in a different way. To do so you must configure I/NET for which specific .UPD file to load by editing ASC.cnf. It is located within the I/NET Seven Data subdirectory and the default path is I/NET Seven\Data\ASC.cnf.

  1. As a safety measure, save the default version of the ASC.cnf file, giving it a different name, such as “BackupASC.cnf”.
  2. Open the ASC.cnf text file with MS Notepad text editor.
  3. Find the line that reads "2-4-2.10=AHU_2210".
  4. Place a colon “:” and a space at the beginning of that line. (The colon and space act as a comment flag and I\NET ignores those lines when it's time to download.)
  5. Then find the line which reads ": 2-4-2.10=AHU_2100" and remove the colon at the beginning of that line.
  6. Save the modified ASC.cnf file and close notepad.

This tells I\NET that you want to download the version which controls the economizer damper based on room temperature. The default setting causes I\NET to download the application which controls the damper based on mixed air temperature. The MR-AHU is shipped from the factory with the 2100 application so if you want to change to mixed air control (2210), just update ASC with no changes.

To actually load the UPD file into the controller, open I/NET, connect to the SLI, choose edit-controller-ASC functions. Choose "Update ASC, then select which controllers you wish to change. Click OK and when prompted for the file path, click OK or hit enter. This causes I\NET to download from the default (data) directory.

If this ASC has already been in use and it's point database updated to the SLI, one more step is necessary. The ASC, having just been loaded with the default application, has default designations for the station parameters and point types. The SLI may not have them in the same locations. To force them to be equalized:

  1. Open the MCU_configuration
  2. Select the ASCs in question
  3. Set them to internal
  4. Click OK
  5. Re-open MCU_configuration
  6. Set them back to ASC
  7. Click OK.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1832
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore