Issue
During a Continuum to SmartStruxure 1.2 conversion, getting Unknown Object errors when trying to download to B3 controllers with SmartStruxure.
Environment
- AS
- b3
- Unknown Object
- Error
Cause
Non StruxureWare objects exist in the b3 controller.
Resolution
Set the ACCID of the b3 controller to 0 using a RoamIO.