Unable to turn a Vista Trend on and receive error message "May only be changed in online-mode"
  • Unable to turn a Vista Trend on and receive error message "May only be changed in online-mode"
  • PeterLarsen
    PeterLarsen
‎2018-09-06 02:05 PM
When activating a Vista trend I get the error message "May only be changed in online-mode"
Vista
You have Vista offline. This is indicated by a red cross in the Vista server icon.
To place Vista into Operating mode follow these steps:
  1. Navigate to the object $System in the root directory of the project.
  2. Right mouse click on the object and select properties
  3. Under the general tab check the "Operating" check box
  4. Select the ok button.
The red cross should now disappear and you should be able to activate your trend.
  • 4719