Unable to successfully run a station with BacnetNetwork or add a BacnetNetwork to a running station when WorkBench is installed on Chinese (Taiwan) Windows XP operating system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to successfully run a station with BacnetNetwork or add a BacnetNetwork to a running station when WorkBench is install...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1163 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to successfully run a station with BacnetNetwork or add a BacnetNetwork to a running station when WorkBench is installed on Chinese (Taiwan) Windows XP operating system

Picard Product_Support
‎2018-09-06 01:53 PM

Issue

Attempting to run a station with BacnetNetwork already added will result in the station not being able to start successfully. The station status in Application Director will continuously be shown as 'Starting'.

The following error messages can be seen in the station's output messages.

# A fatal error has been detected by the Java Runtime Environment:
#
#  EXCEPTION_ACCESS_VIOLATION (0xc0000005) at pc=0x0e953cc4, pid=2912, tid=3104
#
# JRE version: 6.0_16-b01
# Java VM: Java HotSpot(TM) Client VM (14.2-b01 mixed mode windows-x86 )
# Problematic frame:
# C  [platform.dll+0x33cc4]
#
# An error report file with more information is saved as:
# c:\niagara\niagara-3.5.34\daemon\hs_err_pid2912.log
#
# If you would like to submit a bug report, please visit:
#   http://java.sun.com/webapps/bugreport/crash.jsp
# The crash happened outside the Java Virtual Machine in native code.
# See problematic frame for where to report the bug.
 


When you try to add the BacnetNetwork to a running station, the station will disconnect. The BacnetNetwork is not added after you re-connect to the station.

Environment

I/A Series G3 versions 3.5.25.4 and later

Windows XP Chinese (Taiwan) Edition

Cause

The BACnet module is unable to correctly process the unicode character set of the computer's Ethernet adapter name. This this case, the Ethernet adapter name contains traditional Chinese characters.

Although it has not been tested or verified, the same problem may occur on computers installed with other unicode languages versions of Windows (Japanese, Korean, Thai etc.).

Resolution

Current workaround is to rename the computer's Ethernet adapter name to 8-bit characters (English etc.).

  1. In Application Director, 'Kill' the station that is 'Starting'.
  2. Rename the Ethernet adapter.
  3. Start the station in Application Director.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5058
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of