Unable to edit the Priority field of a BACnet Schedule as the field is greyed out.
  • Unable to edit the Priority field of a BACnet Schedule as the field is greyed out.
  • AdamSteele
    AdamSteele
‎2018-09-06 10:54 AM
Trying to change the Priority level that the Schedule uses from the default 16 to a higher priority.
Continuum BACnet
Schedule object
The Schedule object has not been discovered on the BACnet side. The BACnet attributes can't be viewed or modified.
Find the Schedule on the BACnet side.
  1. Right-click Root and select Find New BACnet Devices.
  2. Right-click the Device in the BACnet Devices folder and select Send To > Database.
  3. Open the Schedule and change Priority from the default 16 to the required priority level.