Issue
If a Xenta 913 with SNVT(s) is added as a Lon device to an Automation Server Lonworks network the commission process fails in the last step with error 0
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Automation Server
- TAC Xenta 913
- TAC Xenta 700
Cause
This is a bug in the Xenta Server firmware.
Resolution
This issue will be fixed in Xenta 913 firmware version 5.1.9, however hotfixes have been made for 5.1.8 and can be requested from PSS (TACXenta913-5.1.8.15 and TACXenta700-5.1.8.47).
Note: All data will be lost in the Xenta Server when applying the hotfix.