Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Unable to change setpoint on stat connected to Xenta 102-AX

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to change setpoint on stat connected to Xenta 102-AX
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1445 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to change setpoint on stat connected to Xenta 102-AX

Picard Product_Support
‎2018-09-06 12:27 PM

Issue

Cannot adjust the setpoint up or down on STR-250, STR-202 or M/STAT that is connected to Xenta 102-AX. Also, effective setpoint may not be changing when device goes from unoccupied to occupied modes.

Product Line

TAC Vista

Environment

  • Xenta 102-AX Plug-in
  • STR-250
  • M/STAT
  • STR-202

Cause

This problem is most often caused by a scenario similar to the following example:

  1. A 102-AX is in cooling mode with an effective cooling setpoint of 70°F. An STR-250 stat is connected to the 102-AX and has a stat adjustment range (nviSetpoint.SCPTmaxRnge) of 6°F. This allows the occupant to adjust the setpoint ±3°F from the stat.
  2. The occupant is hot and adjusts the stat down to its minimum of 67°F. (3°F less than the cooling setpoint)
  3. The building operator decides that ±3°F is too much adjustment range and changes nviSetpoint.SCPTmaxRnge to 4°F (±2 degrees F) from the front end.
  4. The effective setpoint is still 3°F less than the cooling setpoint but now the stat cannot adjust the setpoint up or down since it steps in .1°F increments and both 66.9°F and 67.1°F are outside of the adjustment range.
  5. Since the stat adjusted setpoint offset is not a visible point and cannot be adjusted from the front end, the setpoint offset will be stuck until the stat adjustment range is expanded to include the effective setpoint and the setpoint offset is changed from the stat.

Resolution

  1. To correct this problem the nviSetpoint.SCPTmaxRnge should be set high enough to include the effective setpoint. This can be done from Vista and can be found in the VAV_Controller object of the 102-AX or it can be done from the 102-AX Plug-in where it is called Stat Adjustment Range and is found on the Operating Parameters page.
  2. The setpoint should be changed at the stat to match the setpoint of the mode in which the 102-AX controller is currently operating. (eg occupied cooling setpoint)
  3. The stat adjustment range can then be returned back to its previous setting and the occupant can adjust the setpoint up or down and it will stay within the limit.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 7849
  • thermostat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now