Unable to Link SIM Block Output in I/A Series R2 UNC – NullPointerException Error
  • Unable to Link SIM Block Output in I/A Series R2 UNC – NullPointerException Error
  • CraigEl
    CraigEl
  • SESA113595
    SESA113595
‎2018-09-06 01:00 PM
Last Updated: Administrator CraigEl Administrator ‎2025-12-10 10:08 PM
In an I/A Series R2 (Niagara) UNC station, attempting to link to the output of a SIM block results in the error:
java.lang.NullPointerException.
TAC IA Series
  • I/A Series R2  UNC with the GCM driver
  • Network 8000 SIM-CCN, containing SIM blocks with TYPE = 44
SIM-CCN blocks with TYPE = 44 can be highly customized. Their inputs and outputs may use “data species” that the GCM driver in the UNC does not recognize.
The GCM driver has not been tested with any SIM variants (SIM-CCN, SIM-MTECH, SIM-TRANE, SIM-YORK, LNC-100).
  1. Use appropriate Shadow Objects such as:
    • GcmAvParam
    • GcmDateParam
    • GcmDvParam
    • GcmEnumParam
    • GcmIntParam
    • GcmStringParam
    • GcmTimeParam
  2. Add APT or DPT blocks to the SIM-CCN database to correctly interpret SIM block outputs for the GCM driver in the UNC.
  • TAC IA Series
Tags (2)
  • 6739
  • CraigEllis25