Issue
java.lang.NullPointerException.Product Line
TAC IA SeriesEnvironment
- I/A Series R2 UNC with the GCM driver
- Network 8000 SIM-CCN, containing SIM blocks with TYPE = 44
Cause
The GCM driver has not been tested with any SIM variants (SIM-CCN, SIM-MTECH, SIM-TRANE, SIM-YORK, LNC-100).
Resolution
- Use appropriate Shadow Objects such as:
GcmAvParamGcmDateParamGcmDvParamGcmEnumParamGcmIntParamGcmStringParamGcmTimeParam
- Add APT or DPT blocks to the SIM-CCN database to correctly interpret SIM block outputs for the GCM driver in the UNC.