Type of Acknowledgement Set to 'Extended' on Sigma Interface Object Alarm and Hardware Alarm

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Type of Acknowledgement Set to 'Extended' on Sigma Interface Object Alarm and Hardware Alarm
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1357 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Type of Acknowledgement Set to 'Extended' on Sigma Interface Object Alarm and Hardware Alarm

Sisko DavidChild Sisko
‎2022-02-28 07:48 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-30 05:19 PM


Issue

After transitioning from Sigma to EcoStruxure Building Operation (EBO), users may notice that alarm clears require acknowledgements. This occurs because the Type of Acknowledgement on Sigma Interface object alarms and hardware alarms is set to 'Extended' and cannot be changed directly to 'Single' within EBO.

set to extended.png

Product Line

EcoStruxure Building Operation, Satchwell Sigma

Environment

  • Building Operation Enterprise Server
  • Satchwell Sigma

Cause

The Sigma Alarm Manager settings are incorrectly configured during the data import process into EBO. Specifically, the Alarm Clear Controls are set to require acknowledgements, resulting in the 'Extended' acknowledgement type.

Sigma Alarm controls now.png

Resolution

To ensure that only alarms (not alarm clears) require acknowledgement in EBO, follow these steps on the Sigma server:

  1. Open Sigma Alarm Manager.
  2. Navigate to:
    Configure > Alarm Controls
  3. Uncheck the box labeled:
    'Alarm Clears Acknowledgeable'

    Sigma Alarm controls after change.png

  4. Redo the Data Import into EBO.

After re-importing, the Type of Acknowledgement should now be set to 'Single'.
If it instead shows 'No', refer to the related article:
Type of Acknowledgement set to 'No' on Sigma Interface object alarm for further guidance.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • CraigEllis25
  • DavidChild22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore