A system had two BACnet Icons in the ContinuumExplorer - one fully populated with controllers and points and the other empty.
CyberStation
BCX
MS/TP
When trying to save a simple PE program mirroring a third party BACnet point, an error "could not find the object" on the path which included the BACnet Devices folder came up.
There should not be multiple BACnet Devices folders in the ContinuumExplorer. In this case the empty BACnet Devices folder was renamed. The InfinityProgram could then resolve the object name and save the program successfully.
Further investigation as to what caused the duplication must be done.