Troubleshooting DMS-Microsmart Bus Communication Issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting DMS-Microsmart Bus Communication Issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1140 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting DMS-Microsmart Bus Communication Issues

Picard Product_Support
‎2018-09-10 03:36 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-21 06:05 PM

Issue

Communication failures with Microsmart controllers on the DMS bus network.

Product Line

TAC IA Series

Environment

Microsmart controllers (all models installed with revision 9.x, 10.x, or 11.x firmware)

Cause

Common causes include:

  • Incorrect power supply wiring or insufficient voltage
  • Shared power between controllers and field devices
  • Exceeding maximum controller count per RS-485 segment
  • Improper network topology or cable type
  • Missing or incorrectly installed End-of-Line (EOL) modules
  • Ground loops or shield continuity issues
  • Duplicate or illegal point names in controller database
  • Faulty line drivers or incorrect address switch settings

Resolution

The following checklist provides several settings/configurations to review when faced with a communication problem at the controller level. The content was compiled from different resources, summarized, and laid out in an easy-to-use manner so as to provide a quick-reference document.

Do all controllers have a power supply?
  • Each takes 24 VAC from a Class 2 transformer
ACTION:
Confirm with a voltmeter.
  • If no voltage present, check on-board fuse and then the local circuit breaker. Note: Do NOT ground the transformer’s secondary when powering a MSC-MPC-001. With other controller types, the secondary is grounded.
  • If voltage is present, must be within tolerances (20.4 to 30 VAC)

Confirm power (VA) requirements.

  • Varies per controller
    (see installation instructions)

Do the affected controllers share a common
power supply?

  • The MSC-MPC-001 must have its own
    DEDICATED power supply
  • Other controller types can share the same
    AC transformer provided the VA rating is
    adequate

ACTION:
Review power wiring

(see installation instructions)

Do the affected controllers share a common
power supply with output field devices?
  • Power for the controllers and power for the output devices MUST REMAIN SEPARATE
ACTION:
Review controller and field device power wiring (see installation instructions)
In addition, avoid wiring any half-wave and fullwave powered devices to the same transformer.
How many MicroSmart controllers exist?
  • Firmware revision 9, 10, & 11 family controllers can communicate on the same RS-485 wire segment simultaneously
  • Maximum per RS-485 segment = 30 (31 if no repeater is installed)
ACTION:
Determine controller count
  • If there are more than 31, a repeater/router is required
  • If there are more than 62, only firmware revision 11 family controllers can be physically addressed higher than 62
Connect the first 30 controllers (isolate any additional nodes) and attempt/stabilize communications.
Any repeaters installed?
  • Allows the connection of two or more RS-485 wire segments
  • Extends the maximum controller count by 30 (maximum of 124 addressable nodes supported)
ACTION:
Identify model number
  • Review settings using its installation instructions
Replace line drivers with known, good ones
(Part# E21-1144)
How rapidly is the Watch Dog Timer (WDT)
LED blinking?
  • Once / second = proper network communication
  • A controller’s logical address is always one higher than the number calculated by the switch settings. For example, if all switches are OFF (binary equivalent of 0), the controller’s logical address is 1. If switches 1 & 2 are ON (binary equivalent of 3), the controller address is 4.
  • Network wire connections ARE polarity sensitive.
ACTION:
Review LED activity
  • No blinking but illuminated
    • Verify proper power requirements & wiring (see installation instructions)
    • Perform a hardware clear (place all address switches in the ON position and power cycle the controller)
  • No blinking & not illuminated
    • Check the on-board fuse
  • Blinking faster than once / second
    • Check the address switch for proper position. Verify address is not duplicated on the network
    • Check the network connector and ensure it is properly inserted
    • Ensure the + wire and – wire are properly identified and the shield wire is also connected.
What is the length and topology of the
controller trunk?
  • Bus Topology
    • Daisy-chain (no tees)
    • 4000ft/1219m maximum wire length
  • Trunk wiring is polarity sensitive
  • Recommended cable: 24 AWG twisted-pair, shielded
    • General Purpose:
      • Under 1000ft, Belden#9501
      • Over 1000ft, Alpha#9823C
    • Plenum & Riser-Rated:
      • Under 1000ft, Belden#89503
      • Over 1000ft, Belden#89182
ACTION:
Review the following:
    • Ensure two EOL modules are installed. Each module must be installed correctly (black dot on module in the same corner as the white dot on the circuit board)
    • Remove each EOL and check for following
    • resistances:
      • Pins 1-8: 3.3 kohms
      • Pins 3-6: 150 ohms
      • Pins 4-5: 3.3 kohms
    • Ensure there are no ground loops in the + and – wires. To do this, use a multi-meter & measure the + and – wires, separately to earth ground
    • Ensure the shield wire is continuous throughout the entire length of the trunk and connected to a solid earth ground in only one location
    • Replace line drivers on the controllers (Part# E21-661). Check trunk voltages:
      • + to earth ground: 2.2 – 2.6 Vdc
      • – to earth ground: 2.2 – 2.6 Vdc

      If 0 Vdc or 5 Vdc is detected, check other controllers for bad line drivers.

Determine cable used. If it is shielded, connect it to earth ground in ONE location through a 470 kK, ¼ watt resistor. The shield must be continuous throughout the wire segment.
What is the condition of the controller database? ACTION:
Review the controller database
  • Illegal point names must be corrected.
    • Illegal characters are: / # * : ; $ = | &.
  • Duplicate point names must be corrected
Will Operator Interface (Part# PS-OPRIF) communicate to the controller?
  • Direct connection to a controller can only be done with the Firmware Revision 10 & 11 Families
  • Accessing a networked controller through a direct connection using a MSC-LIM is possible but very slow (300 baud maximum). It is only recommended for checking communication status and not for application programming. It will also require a master controller (DMS35/350A/3500)

ACTION:
Attempt an upload of the controller database

  • Requires a Laptop Interface Module (Part#
    MSC-LIM)
  • Operator Interface version 11.41 and 11.6
    both support direct connection to a controller
  • If communication fails to work, try another
    controller to eliminate the pc and interface
    cabling from the troubleshooting process
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 5971
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore