Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Troubleshooting TAC Network Variable (TANV) Communication

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting TAC Network Variable (TANV) Communication
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Trey_Boothe
    Trey_Boothe
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2423 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting TAC Network Variable (TANV) Communication

Picard Product_Support
‎2018-09-07 02:09 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:33 PM

Issue

Xenta programmable controllers can communicate to each other using TAC Network Variables (TANV). These are defined in the Menta programming and travel on Xenta Group Bindings in the LNS environment. If data is failing to update in the receiving controller, there are a few troubleshooting techniques that can help.

Product Line

TAC Vista

Environment

  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta
  • LonMaker/NL220

Cause

TAC Network Variable communication can be compromised for four reasons:

  • Network path not defined correctly in the Menta file
  • Network path name is too long
  • Group Bindings not done correctly in LonMaker/NL220
  • Controller's network output capacity has been exceeded

Resolution

Verify the Network Path

If the network variable has been populated by browsing Menta files on the hard drive, or was entered manually, it can be the cause of the problem. Even visual inspection of the network path is not 100% reliable -- a lowercase "l" and an uppercase "I" appear the same, for example. The only way to be certain the path is correct is to browse it in through the Vista database.

  1. Open the Menta file from the Vista database. Right-click on the receiving controller and select Edit.
    Editing a Menta file directly from the hard drive of a computer does not give you the same network browsing options and can lead to incorrectly mapped network variables.
  2. Double click the network variable AI block and go to the Bind dialogue.
  3. Next to the Network Address text field is a browse button ("..."). Click it to open the network browse window. This tree structure should be the same as the folder view in Vista Workstation.
  4. Navigate to the sending controller's public signal and click okay.
  5. Download the application to the controller.

Verify that the Network Path Name is not too long

If the network variable path name, or the Network Address, is too long then this will cause a problem.The network variable path name, if the point is in a module, looks like ControllerName\ModuleName\PointName. If it is not in a module then it will have the Program Specification name instead of a module name. So it would look like ControllerName\ProgramSpecificationName\PointName.  If the ModuleName\PointName or ProgramSpecificationName\PointName part of the path is longer than 33 characters, counting the "\", then it will not work.

Verify Group Bindings are correct

  1. Refer to Verifying Xenta Group Bindings in an LNS system for the procedure on verifying group bindings.
  2. If the group bindings are not correct, redo group bindings and download the sending and receiving controllers.

Calculate the total output of the controller

Depending on the controller type, there are different limits on the network variable outputs.  This includes both SNVTs and TANVs.  If together, they exceed the capacity, there will be spotty updates and random signals that don't make it to the receiving controller.  Unfortunately, there is no easy way to count the TANVs.

  1. In the Menta file of the sending controller, go to Options > Memory Usage... > Advanced...
  2. Make note of the TACNV/SNVT Out Free number.  Each SNVT output defined in the Menta file consumes one of these outputs and decreases the number of Free signals available for use with a TANV.
  3. The only way to count the number of network variable outputs is to know each receiving controller that is pointing back to the sending controller with a TANV. 
  4. Unlike with SNVTs, EACH signal in EACH receiving controller consumes one of these available outputs.  If the output limit has been exceeded, the communication will suffer.
  5. Reduce the number of network variables coming from one controller by "cascading" signals.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4900
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore