Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Troubleshooting RSTP with Wireshark

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting RSTP with Wireshark
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
1156 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting RSTP with Wireshark

David_Purser Champion
‎2025-09-30 10:36 AM

Issue

Need to perform a diagnostic verification as a preventative measure during routine maintenance or reactively in response to cabling that is causing RSTP issues.

Product Line

EcoStruxure Building Operation

Environment

  • Multi-purpose Controller (MP-C)
  • Multi-purpose VAV (MP-V)
  • Room Controller (RPC)
  • IP-IO

Cause

Cabling or cabling terminations between controllers in the RSTP loop can cause issues.

Resolution

  1. Reference RSTP Troubleshooting for BACnet/IP Controllers - Schneider Electric Community to ensure that:
    1. the managed switch is appropriately configured for RSTP
    2. all SpaceLogic controllers, on the RSTP loop, report RSTP Status = Operational
  2. Leave one side connected to the managed switch, plug the free end into the laptop running Wireshark, and take a capture.
  3. Ensure both ends are unplugged
  4. Plug the other side into the managed switch, plug the free end into the laptop running Wireshark, and take a capture. RSTPWiringConfigurationDuringTesting.png
  5. Evaluate based on the information below
  6. If either evaluation fails, check the cables based on Message Age using a cable tester. It is optional but highly recommended to use a cable tester that displays cable length, as it tends to be more accurate and can point out failures that other testers may report as passing.
  7. If it passes the evaluation on both ends, then one can plug both ends into the managed switch

Evaluation

This capture shows a topology change (TC + Root) in RSTP, then settles out to a consistent Root Bridge Priority and Message Age. Your capture should only show a topology change when Wireshark is capturing on one end and the other end is connecting/disconnecting from the managed switch.

STPSample.png

Review the following fields:

  • Root Bridge Priority - should be consistent and show the Priority of the Root Bridge. The root bridge can be the switch to which the RSTP loop is connected or a managed switch upstream.
    • If it shows 32768, then another SpaceLogic controller assumed the root because it is not communicating properly back to the root bridge. (See Message Age Note)
  • Message Age - should be consistent and show the expected number of controllers away from the root bridge.
    • When Root Bridge Priority is 32768, you can use Message Age to determine how many controllers away the issue is occurring, and check the cabling connected to or near that controller.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • DavidPurser25
  • DavidPurser26
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore