Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

RSTP Troubleshooting for BACnet/IP Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • RSTP Troubleshooting for BACnet/IP Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
13 Likes
15313 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

RSTP Troubleshooting for BACnet/IP Controllers

David_Purser Champion
‎2023-03-23 09:05 AM

Issue

BACnet/IP controllers are not configured in RSTP Mode by default, therefore must be configured during installation. Having RSTP Mode disabled by default allows one to connect BACnet/IP controllers to any switch, even with port security configured to detect BPDU packets and disable the port.

Product Line

EcoStruxure Building Operation, TAC IA Series

Environment

  • Multi-purpose Controller (MP-C)
  • Multi-purpose VAV (MP-V)
  • Room Controller
  • IP-IO
  • I/A Series N4 Jace8000
  • SmartX IP Driver for Niagara

Cause

RSTP protocol requires that controllers, switches, and network architecture are configured to ensure the protocol will operate as expected. 

Resolution

Setting RSTP Mode for BACnet/IP Controllers

ALL devices in the RSTP loop MUST BE IN RSTP MODE to function properly. This is not a huge issue because during startup you can unplug 2nd side of the loop and it will function properly in a daisy chain.

  1. Ensure the SmartX Controllers are configured correctly Configuring BACnet/IP Controller Device Settings
    1. A factory or network reset returns the RSTP setting to Disabled.
    2. Important: Whenever you change RSTP settings, the controller MUST be WARM START. If you fail to perform this restart, the BACnet/IP controller will continue communicating using its previous RSTP settings. 'Activate IP Changes' does not affect RSTP mode.
  2. Ensure the switch is configured correctly per Configuring RSTP on a Managed Switch for SmartX IP Controllers. If asked to review this for a case, please provide PSS screenshots from the switch configuration page(s). 
    • Bridge Priority = 4096
    • Hello Time = 2 sec
    • Max Age = 40  (40 is the maximum value allowed by the protocol. Default is 20)
    • Forward Delay = 21 sec
    1. Bridge Priority Considerations
      1. Change Bridge Priority by adding 4096 as switches get further away from AS. (8192, 12288, 16384, 20480, 24576, 28672)
      2. DO NOT set the priority as 32768 or higher because that is the built-in Bridge Priority of BACnet/IP Controllers.
      3. First, configure the Root Bridge Switch (closest to the Automation Server) settings. Then, configure the additional Switches in order of increasing Bridge Priority.
    2. {OPTIONAL}: Troubleshooting RSTP with Wireshark
    3. Plug in 2nd side of the RSTP Loop
      1. If all devices stay online, then it is working properly. Now test line breaks or controllers that are powered off.
      2. If all devices go offline and/or the switch LED is flashing rapidly, then go to RSTP Troubleshooting.

Managed Switch Troubleshooting

  1. Consult the documentation or contact the vendor or manufacturer to assist with configuration for the items below.
  2. Ensure the switch is IEEE 802.1D - 2004 capable. BACnet/IP Controller Networking Term Definitions RSTP Ring mentions the Rapid Spanning Tree Protocol is specified in IEEE 802.1D - 2004.
  3. Ensure the firmware is up-to-date by contacting the vendor or manufacturer or downloading it from its website.
  4. Ensure ports not participating in RSTP are configured as Edge Port, Admin port, or have STP disabled. Nomenclature for those settings on your specific managed switch may vary.
  5. Adding BACnet/IP controllers to site-managed switches, work with Local IT to add these devices to their network. They will need to work with their switch vendor/manufacturer/support group to ensure the configuration of those switches because it could be more complex than changing the minimum recommended four settings above. Also, since RSTP Protocol is limited to Max Age = 40 (hops including site switches and BACnet/IP controllers), each loop's size may be limited based on their site switch network configuration and architecture. 
  6. Determined the proper configuration (or disable) for the following features.
    1. DHCP snooping
    2. Dynamic ARP inspection
    3. Denial-of-service (DOS) mitigations
    4. BPDU Guard
    5. BPDU Filter
    6. Energy-saving settings. Similar to Wake-on-LAN: the switch had minimal traffic, so ports entered power-saving mode. When they reactivated, the AS-P had already timed out, triggering a comm loss alarm.

RSTP Troubleshooting

Check each BACnet/IP Controller -> Diagnostics -> Device Report to confirm in RSTP Mode

      1. MANUAL CHECKOUT
        1. Double-click MP - Diagnostics Files - Device Report
        2. It will open in the default text editor
        3. Review the Device Settings section near the bottom.
        4. In firmware 1.00.0x, the report should report RSTP Mode: Enable
        5. In firmware 2.00.0x or higher, RSTP: Enabled and RSTP Status: Operational
        6. If it reports disabled, then perform Setting RSTP Mode for BACnet IP Controllers Step 1 until RSTP is working properly.
      2. USE SEARCH & EVENTS
        1. EBO 2.x MP Device IP and Settings.xml for EBO 2.0 as it only includes MP controllers
        2. EBO 3.x SmartX Device IP and Settings.xml for EBO 3.x or higher
        3. Import attached search
      3. USE RSTP STATUS GRAPHIC IN WEBSTATION
        1. Run from web browser via WebStation because utilizes ClientAPI
        2. EBO 6.0 and higher: TGML HTML Version
          1. SpaceLogic RSTP Status Summary - Schneider Electric Community 
        3. EBO 3.1 and higher: TGML Script Version
          1. Frontline Fridays Episode 02 - Rapid Spanning Tree Protocol (RSTP)
            1. Date: 2022-11-11
            2. Mike Botens posted the following in the thread:
              1. RSTP Status TGML dated 2022-11-09
              2. PDF of the presentation
          2. Fusion Fridays - Session 07 ​​​​
            1. Date: 2020-05-28
            2. The start of the video shows the graphics page in use
            3. RSTP Status.zip is downloaded via the link below the video.
            4. Extract the TGML and drop it on the AS to import. The suggestion is to store TGML directly under the AS to help with navigation in Webstation.
            5. Bind the network to the BACnet/IP network with the BACnet/IP Controllers. (You may need a second TGML page if BACnet/IP controllers are on Primary and Secondary IP)
            6. Run from web browser via WebStation because utilizes ClientAPI

KNOWN ISSUES

    • Offline controllers that are scattered are NOT an RSTP issue. Check to see if there is a possible DHCP issue by verifying controllers are still at their AUTO-IP address (IP 169.254.nnn.nnnn Subnet Mask 255.255.0.0). RSTP communications issues affect the entire RSTP loop or one contiguous group of controllers.
    • Factory Reset or controller replacement should leave one ethernet cable unplugged until configured for RSTP per these articles: Replace a BACnet/IP Controller in an RSTP Ring Network Workflow and MP Controller Reset Modes
    • If BACnet/IP Controller Device Report OR RSTP Graphic reports RSTP Status: Changes Pending instead of RSTP Status: Operational, disable RSTP Mode, Warm Start, re-enable RSTP Mode, Warm Start, and check again.
    • SmartX is now SpaceLogic.
    • KNOWN ISSUES with Firmware affecting RSTP:
      • If Firmware 3.02.01 is installed, please upgrade to 3.02.02.
      • RSTP not performing as expected with Static IP addressing
      • RSTP does not work well on RPC HW RPC-16-B HW revision 6
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Attachments
EBO 2.x MP Device IP and Settings.xml
EBO 3.x SmartX Device IP and Settings.xml
Tags (3)
  • Find more articles tagged with:
  • DavidPurser23
  • DavidPurser24
  • DavidPurser26
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore