Issue
MNB controllers do not have internal trend log capability.
Product Line
TAC IA Series
Environment
- I/A Series MNB controllers
- I/A Series R2/G3/N4 Jace
- Building Operation Automation Server
Cause
The MNB family of controllers does not have internal trend log capability. To log these internal calculated values, a different method must be used to allow the values to be logged in an EBO Automation Server or a Jace
Resolution
The BACnet objects "Analog Monitor" and "Binary Monitor" in the Workplace Tech tool may be added to an MNB controller application program. When connected to internal data values in the application, the values can be uploaded to an EBO Automation Server or a Jace for trend logging.