Transferring VisiSat Licenses Between PCs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Transferring VisiSat Licenses Between PCs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1402 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Transferring VisiSat Licenses Between PCs

Picard Product_Support
‎2018-09-07 02:11 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-10 09:05 PM

Issue

Users need to transfer VisiSat licenses from one PC to another, typically due to hardware replacement or system upgrades.

Product Line

Satchwell MicroNet

Environment

Satchwell VisiSat 2.x

Cause

Licenses are tied to the original PC and must be exported and re-imported to function on a new machine. This process is necessary when:

  • Replacing or upgrading a PC
  • Consolidating engineering tools
  • Migrating from VisiSat v2.0 to v2.1

Resolution

Follow these steps to transfer VisiSat licenses:

  1. Export License from Original PC

    • Use the VisiSat license management tool to export each license file.
    • Save the exported files to a secure location (e.g., USB drive or network share).
  2. Transfer License Files to New PC

    • Copy the exported license files to the target PC.
  3. Import License on New PC

    • Use the license management tool on the new PC to import the license files.
    • Ensure VisiSat v2.1 is installed before importing v2.0 licenses.
  4. Reference Documentation

    • For detailed steps, refer to the Moving VisiSat Licenses PDF extracted from the VisiSat Engineering Guide.
    • Also see: Transferring VisiSat version 2.0 license to Computer running VisiSat 2.1
Labels (1)
Labels:
  • Satchwell MicroNet
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4904
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore