Totalising Alarms Using Programmable Points in BAS or Sigma
  • Totalising Alarms Using Programmable Points in BAS or Sigma
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
‎2018-09-06 12:41 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-20 05:06 PM
In BAS or Sigma, users may attempt to totalise multiple alarm points using the + add function in programmable points, such as:
10 XFlo = POINT 0|14 ALARM + POINT 0|15 ALARM + POINT 0|16 ALARM
20 YFlo = POINT 0|17 ALARM + POINT 0|18 ALARM + POINT 0|19 ALARM
30 RETURN VIA TEXT 91 VALUE XFlo + YFlo
While this compiles in the programmable point editor, it does not function correctly in the BAS or Sigma controller.
Satchwell BAS & Sigma
The Sigma controller does not support direct arithmetic operations on alarm points using the + operator. This limitation leads to compilation success but runtime failure.
To correctly totalise alarms, rewrite the programmable point using conditional logic. Here's a working example:
10 XFLO = 0.0
20 IF POINT 0|14 ALARM THEN XFLO = XFLO + 1.0
30 IF POINT 0|15 ALARM THEN XFLO = XFLO + 1.0
40 IF POINT 0|16 ALARM THEN XFLO = XFLO + 1.0
50 IF POINT 0|17 ALARM THEN XFLO = XFLO + 1.0
60 IF POINT 0|18 ALARM THEN XFLO = XFLO + 1.0
70 IF POINT 0|19 ALARM THEN XFLO = XFLO + 1.0
80 RETURN VIA TEXT 91 VALUE XFLO
If the number of alarm points exceeds the token limit for a single programmable point, split the logic across multiple points and combine them:
10 XFLO = (POINT 0|a + POINT 0|b + ...)
20 RETURN VIA TEXT 91 VALUE XFLO
  • Satchwell BAS & Sigma
Tags (3)
  • 7296
  • CraigEllis25
  • summary