Should the Touchscreen "Time Master" setting still be set, when the Touchscreen is connected to a Xenta 555?
Micronet
Xenta 555
The Touchscreen would normally be configured as a "Time Master" when not connected to a Xenta 555.
The functionality remains the same, the Touchscreen is set as a "Time Master" and will broadcast the time every 10 minutes, by default.