The Xenta Repeater Provides Signal Restoration and Conditioning on LON Networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Xenta Repeater Provides Signal Restoration and Conditioning on LON Networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1504 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Xenta Repeater Provides Signal Restoration and Conditioning on LON Networks

Picard Product_Support
‎2018-09-10 12:14 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-02 06:15 PM

Issue

LON networks may experience communication issues due to excessive physical length or a high number of connected devices. The Xenta Repeater helps mitigate these issues by restoring and conditioning signals, enabling longer network spans and supporting more devices.

Product Line

TAC Vista

Environment

  • Vista Lon Networks
  • Xenta Repeaters (Part # 007309120)

Cause

LON communication failures often stem from:

  • Exceeding recommended cable lengths
  • Overloading the network with too many devices

Resolution

The Xenta Repeater:

  • Uses a standard Xenta 400 base
  • Splits a LON channel into two segments
  • Connects one segment to COM 1 terminals, and the other to COM 2 terminals

🔍 Note:

  • A LON channel is a section of the network separated by a router.
  • A segment is a portion of a channel divided using a repeater.

📏 Cable Length Guidelines

Cable Type Max Bus Length (Doubly Terminated) Max Node-to-Node (Singly Terminated) Max Segment Length (Singly Terminated)
Belden 85102 2,700 m / 8,858 ft 500 m / 1,640 ft 500 m / 1,640 ft
Belden 8471 2,700 m / 8,858 ft 400 m / 1,312 ft 500 m / 1,640 ft
UL Level IV 22AWG 1,400 m / 4,593 ft 400 m / 1,312 ft 500 m / 1,640 ft
Siemens J-Y(st)Y 900 m / 2,953 ft 320 m / 1,050 ft 500 m / 1,640 ft
TIA568A Cat.5 900 m / 2,953 ft 250 m / 820 ft 450 m / 1,476 ft

📌 Design Rules

  • Max 128 devices per LON channel
  • Max 64 devices per segment
  • Up to 2 repeaters per channel (max 3 segments)
  • If no router is used, only 64 devices allowed (single segment)
  • Recommended: ≤ 50 devices per segment for flexibility during installation

🔄 How It Works

The Xenta Repeater contains:

  • Two internally connected LON transceivers
  • Transient suppression circuits

It:

  • Reads LON packets from one segment
  • Re-broadcasts them to the next segment
  • Filters out noise, ensuring clean signal transmission

Unlike simple amplifiers, it does not amplify noise, resulting in strong, noise-free communication across segments.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 5656
  • MikaelKrantz25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore