The OrOr object in MNB controllers always reports that it is "ON".
  • The OrOr object in MNB controllers always reports that it is "ON".
  • RandyDavis
    RandyDavis
  • sesa116877
    sesa116877
‎2018-09-06 02:18 PM
Last Updated: Guinan RandyDavis Guinan ‎2022-03-31 08:11 AM
TAC IA Series
  • I/A Series WorkPlace Tech
  • I/A Series MNB Controllers
Input to the OrOr object is inverted and has nothing attached to it.
When an "OR" input property of a logic object is inverted with nothing attached to it, the input will be seen as an "Off," resulting in an output of 100.
If the input of an OrOr object is not connected to I/A Series BACnet controller, an "OR" input should not be inverted.   If another object outputting a "NA" is attached,  the "OR" input will function correctly.