Issue
When you browse a Lonmaker object, the temperatures display the incorrect units.
Environment
Lonmaker
Windows XP
Cause
The regional settings on the computer are incorrectly set for the systems specific region and therefore show the incorrect units for temperature.
Resolution
The Regional Settings of your PC need to be correctly configure for your Region. The steps to correct this are:
- Navigate to Control Panel
- Open Regional and Language Options
-
Under the Regional Option tab ensure the correct region is selected
-
Select the Advanced tab and ensure that the correct Non unicode region is selected.
- Reboot the computer after these changes have been made.
- If you have updated the Vista database with these object you will need to delete them from the TAC Network in the System Plug-in. Then update the Vista Database without the effected controllers.
- Once the database has been updated to remove these effected controllers you can let the plug-in update the TAC network. After the TAC Network update a Vista database update can be done. This will transfer the XIF files and set them to the correct units.
- Check the database for any links on these updated items and correct lost object paths.