Temperature Sensor Resistance Charts
  • Temperature Sensor Resistance Charts
‎2020-12-02 06:46 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 03:44 AM
Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista
Temperature Sensors
Temperature (°C) to Resistance Charts (ohms).
Upgrading the site BMS, but retaining the existing sensors and the sensor resistance values are not known.
The resistance of a sensor at a specific temperature can be downloaded below, there are a number of tables collated from different sources for a number of Schneider Electric sensors and other BMS suppliers.
In EBO, the thermistor selection in the IO module or controller does not represent the thermistor bead type, an example is the Continuum Type I in EBO, but the bead is a Type 3,. For further information regarding this see the KB article  Thermistor type selection in EBO.
The document All Sensors covers the following:
  • Satchwell DxT sensors are replaced by STR600, STP660, STD600, STO600 type T with shunt, and use the Satchwell T range chart
  • Drayton DC1000, DC1100 30K6A1 is now known as STR600D, STP600D, STO600D
  • Andover 10K4A1
  • TAC Inc. Vista 1.8KA1
  • I/A series 10K3A1 with 11K shunt
  • INET 10K2A1 (10k Dale)
  • BALCO 1000 ohm RTD
Older Satchwell ranges:
  • Satchwell DW1204, DW1305, DWS1202
  • Satchwell DO
  • Satchwell DD/DR
Other manufacturers included:
  • Allerton 3K3A1
  • Ambiflex 2012, Honeywell Aquatrol, Jel/Thorn, Trend, York 10K3A1
  • Schlumberger (air) 5K3A1
  • Schlumberger (immersion) 100K6A1
  • Automatrix, York, Sibe 10K4A1
  • Honeywell 20K6A
  • Landis & Gyr
  • PT100A, PT1000A
Further information regarding INET, IA, the document Thermistor Types Tables (Veris Industries) is available.  The 1k Balco resistance chart is also available.
Further information for the Continuum ACC Temp 10K Type 3 also known as 10K4A1, the document Thermistor Temp Resist Chart (Precon Thermistors) is available.
TC900 series
TC900 RS-03 sensor chart
For I/A Series Controllers (MNL/MNB)
Compatible sensors that have a built-in 11k shunt resistor include the
  • TS-5711-850
  • TS-57011-850
  • TS-57031-850
  • TSMN-90110-850 Series
Any sensor that matches resistance to temperature curve for a 10K Thermistor Type G (U.S. Sensor), Type 9 (Dale/Vishay) or Type III (ACI Series AH) can be used with the I/A Series MNL and I/A Series MNB series controllers, provided that a 11k ± 0.1% 1/8 watt resistor is wired in parallel with the sensor.
The input has a range of -10 to 135 °F (-23.3 to 57.2 °C) with an accuracy of ±1% of span.
Temperature / Resistance Reference Values
Temperature
Deg F (Deg C)
Resistance Resistance
Incl. 11k Shunt
32 (0) 25490 8,012
68 (20) 12,260 5,798
75 (25) 10,000 5,238
104 (40) 5,592 3,707
140 (60) 2,760 2,206
The full temperature/resistance table for the US Sensor 10K Thermistor R-T Curve Type G sensor. Please note that the controller may not be able to use the full temperature range shown in the table.
Labels (8)
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
Tags (10)
  • 5695
  • celsius
  • centigrade
  • DavidChild21
  • GaryMontague21
  • GaryMontague23
  • HernanUruena23
  • LeoTantalo20
  • look
  • RobertAndriolo21
79% helpful (11/14)