Issue
Although data is read correctly from the TSI Pressura RPM20 Hospital Room Pressure Monitor when integrated to a SmartStruxure Solution Automation Server, Modbus read errors and framing errors are seen.
Product Line
EcoStruxure Building Operation
Environment
- SmartStruxure Solution Automation Server
- SmartStruxure Solution Automation Server Premium
- Modbus RTU
Cause
The instruction manual from the manufacturer incorrectly lists the Modbus communication parameters for the RPM20 as 9600 baud, 8 data bits, 2 stop bits and no parity.
Resolution
Investigation of the data from the device shows that the Modbus communications parameters are:
- 9600 baud
- 8 data bits
- 1 stop bit
- No parity
Ensure that these parameters are set in the Automation Server Modbus Master Network configuration.