TC300 thermostat cooling only operation
  • TC300 thermostat cooling only operation
  • CraigEl
    CraigEl
‎2018-09-07 10:59 AM
Last Updated: Administrator CraigEl Administrator ‎2023-07-10 07:38 PM
In applications where heating is not required is it possible to change the thermostat operation to cooling only?
Field Devices
TC300 thermostat
By default the TC300 thermostat is configured for heating and cooling. It should be possible to lockout operation of heating in cooling only applications so that the user cannot inadvertently change modes.
In thermostat model TC303-3A2DLS parameter item 7 allows selection of cooling or heating only mode.
  • Field Devices
Tags (2)
  • 14901
  • CraigEllis23
100% helpful (1/1)