TAC Xenta Server conversion to EcoStruxure Building Operation (EBO)
  • TAC Xenta Server conversion to EcoStruxure Building Operation (EBO)
  • Jonas_Brissman
    Jonas_Brissman
  • DavidChild
    DavidChild
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 07:40 AM
Last Updated: Janeway Jonas_Brissman Janeway ‎2022-08-12 02:00 AM
In the Xenta Servers, it is possible to set the communication port to RS232 or RS485.
In EBO this is not possible on the Automation Server (AS)
  • Building Operation Automation Server Premium (AS-P)
  • Xenta 500
  • Xenta 700
  • Xenta 900
The AS serial ports are RS-485, not RS-232.
There are two solutions to consider when Xenta is using an RS-232 connection:
  • If the connected device also has a RS-485 connection switch to that. (Optionally replace the device with one that has RS-485.)
  • Use a RS-232/RS-485 converter. The converter must have automatic data direction detection and control on the RS-485 side, since our Automation Server devices have no RTS signal (to enable the transmitter) available externally.