Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

TAC Vista will not dial out to a Xenta 901 network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TAC Vista will not dial out to a Xenta 901 network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa115370
    sesa115370

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1409 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TAC Vista will not dial out to a Xenta 901 network

Picard Product_Support
‎2018-09-10 12:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:42 PM

Issue

TAC Vista will not dial out to an Xenta 901 network as expected e.g. when opening a graphic or selecting a remote controller in the folder view.

Product Line

TAC Vista

Environment

  • TAC Vista 4
  • TAC Vista 5

Cause

The COM port and /or the Xenta 901 network are not correctly configured.

Resolution

  1. Check that Vista is in Operating mode. See Opening a graphic will not cause TAC Vista to dial out to a Xenta 901 Network for details.
  2. Check that the COM port your modem is connected to is correctly configured in Vista. The port object in Vista will be of the type 'Communication Port - Modem'. Hopefully, it will have a meaningful name relating to the connected modem. In the properties for the port check that the Device Address refers to the correct physical COM port. The Device Address is of the form "server_name-COM_xx", where COM_01 will be the first port defined in Vista. If you have multiple COM ports or a USB/RS232 converter, this may not be the address you want. You can manually change this to the required port: for example COM_03. You can see which physical ports are available in Device Manager.
  3. In the properties for the port check that Traffic direction is set for outgoing traffic. Normally you will set this to "Incoming and outgoing traffic", but you might want "Only outgoing traffic" if you don't want to receive alarms or trend logs via this modem.
  4. Check that the port has been assigned to the Xenta 901 Network. In the properties for the Xenta 901 Network - Modem select the "Ports" tab. This displays a table listing all the communication ports this network will use. If the table is empty Vista will attempt to dial out on all ports not set as "Only incoming traffic". If you have multiple ports this is probably not what you want, so use the Add and Delete buttons to select only the ports that you want this network to use.
  5. In the properties for the Xenta 901 Network - Modem select the "Outgoing Traffic" tab. Check that the phone number shown is correct for the remote site. If Vista is dialing out through a PABX, prefix the phone number with "9,". The comma after the nine tells the modem to wait 1-5 seconds (adjustable via your modems command set) so that a dialing tone can be obtained from the PABX.
  6. If you are using the recommended US Robotics modem, the many default parameters for the comm port and the Xenta 901 Network - Modem should let Vista dial out without further modification.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7430
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of