TAC Vista IV and Peripheral Software Installation Outline

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TAC Vista IV and Peripheral Software Installation Outline
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2336 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TAC Vista IV and Peripheral Software Installation Outline

Picard Product_Support
‎2018-09-06 03:03 PM

Issue

TAC Vista and Peripheral Software Installation Outline

Product Line

TAC Vista

Environment

  • Microsoft Windows 2000/XP (Microsoft)
  • LonMaker (Echelon)
  • Microsoft Visio
  • PCLTA-10/PCC-10/PCLTA-20/SLTA-10/PCNSI
  • Adobe Acrobat 
  • LNS 
  • lmw31.exe
  • lmw313U1.exe
  • LNS3SP8.EXE
  • LNSSP8U1.EXE
  • HASP device driver
  • h4_hinstall
  • hdd32.exe
  • Privilege Licenser 2.01
  • Aladdin Privilege Administrator 2.01
  • taclicense201.exe
  • taclicense202.exe
  • .NET Framework 1.1
  • TACVistaConfig1.2.0
  • .NET Framework 1.1 SP1
  • Microsoft SQL Server (MSDE)2000 SP4
  • MSXML 4.0
  • MDAC 2.8
  • Vista Server IV
  • WorkStation
  • TAC ToolPack 4.X  

Cause

The correct installation procedure for Vista IV and necessary peripheral software.

Resolution

Below is an outline that can be followed to install Vista in the proper order. Each "*" denotes a software package followed by the associated files/programs that are included.

Depending on your specific application, some of the software may not be needed. For example, a Vista Classic network will not need LonMaker. Call Tech Support if you have any questions concerning the software needed for your application.

*Microsoft Windows 2000/XP (Microsoft)

*LonMaker (Echelon CD)
LNS Utilities:
Microsoft Visio, PCLTA-10/PCC-10/PCLTA-20/SLTA-10/PCNSI (only if using an Echelon LNS interface), Adobe Acrobat (if you don't already have it)

*Update LonMaker to 3.13 and LNS to 3.08.05 (TAC Extranet) lmw31.exe, lmw313U1.exe, LNS3SP8.EXE, LNSSP8U1.EXE

*HASP device driver utility (TAC Extranet)
h4_hinstall - MUST Execute from a Command Prompt! or...
hdd32.exe if using Windows Server 2003

*Privilege Licenser 2.01 - "taclicense201.exe" or 2.02 - "Privilege Windows XP crash hotfix" (TAC Extranet)

*.NET Framework 1.1 (Microsoft)

*TACVistaConfig1.2.0 (TAC Extranet)
.NET Framework 1.1 SP1, Microsoft SQL Server (MSDE)2000 SP4, MSXML 4.0, MDAC 2.8
(Reboot)

At this point you could be prompted to choose which type of Licensing to be used. Select which option is best for you, the Site License (Order Entry Department), 30 Day Demo (TAC Extranet), or Engineering dongle. This will write the appropriate license files to the Privilege License Server.

*Vista Server 4.X with WorkStation (TAC Extranet)
(Reboot)

*TAC ToolPack 4.X (TAC Extranet)

If you encounter any errors during the installation process, be sure to make a note of specific errors received so Technical Support can better troubleshoot your issue. A simple way to record errors are to capture a "screenshot" (Ctrl+PrintScnr). The screenshot can then be pasted (Ctrl+V) into Paint a text editor like wordpad for later reference.

Note: Beginning 2012, PSS will no longer support the Privilege License System. The Tamfs26 Server will be retired along with TAC License Server software. It would be wise to inform the customer of this important information to plan for future upgrade in the event that their site license has issues.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2165
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore