Sunrise/Sunset Time Schedules I/NET Seven rev 1.xx and 7780 Lighting Controllers.
  • Sunrise/Sunset Time Schedules I/NET Seven rev 1.xx and 7780 Lighting Controllers.
  • Roger_Bently
    Roger_Bently
‎2018-09-06 03:28 PM
I/NET Seven 2.30 and lower
Model 7780 DLCU Firmware 5.09 and below.
There was an issue in I/NET 2.3 and lower where the Time Schedule for Sunrise and Sunset would not work on 7780 Lighting Controllers.
To work around this issue in 2.3, these steps should be followed:
  1. Go to the Resident IO Point that is controlling the Lights.
  2. Go to the TS Extension and Modify.
  3. Add a Start action on #3 at midnight.
This would re-enforce the timer to start again.
This has been corrected in firmware release 5.10 for the Model 7780 DLCU (Firmware release with I/NET Seven 2.31). To eliminate the issue, and upgrade will be required.
  • TAC INET
  • 1026