Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Sunrise/Sunset Settings on a PCU

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sunrise/Sunset Settings on a PCU
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Roger_Bently
    Roger_Bently

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1548 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sunrise/Sunset Settings on a PCU

Picard Product_Support
‎2018-09-07 01:14 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-24 02:44 PM

Issue

Sunrise/Sunset Settings on a PCU

Product Line

TAC INET

Environment

  • I/NET PCU
  • Sunrise/Sunset Time Schedule

Cause

Are you using Sunrise/Sunset settings on a PCU to control lights and they are turning on and not off when they should? There could be several things that would cause this not to function properly:

  1. Do you have the correct Latitude/Longitude and Zone Settings?
  2. Are you using a 0-Stop for Sunrise and 1-Start for Sunset?
  3. Are you using the correct Control Descriptions for Time Schedules?

The TS in the PCU sends a 0 command (first of the pair) to the control point for the Start action and a 1 command (second of the pair) for the Stop action. If the Control Description pairs in your application are set to send a 0 (de-energize) command as a Start then simply switch the Sunrise action to be a Start and sunset to Stop.

Resolution

There are a couple of workarounds to this issue depending on the way the relays are terminated and the settings for the first of the pair in Control Descriptions.

  1. Using the Sunrise/Sunset settings, a third start command for 1 minute after midnight (12:01 AM) sends a re-enforce command to the controller.
  2. Use actual times instead of sunrise/sunset as long as the times used are well after both the Sunrise /Sunset settings have elapsed.
  3. Verify the correct latitude and longitude are set. Here is a website to check the exact location: www.airnav.com.
  4. Additional information on the Airnav site and a new work around.
Labels (1)
Labels:
  • TAC INET
Attachments
DFWAirnav.ZIP
Tags (1)
  • Find more articles tagged with:
  • 2350
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore