Storage Temperatures for TAC BCX/I2/b3 Controllers
Select a Country
  • Storage Temperatures for TAC BCX/I2/b3 Controllers
  • Alan_Wood
    Alan_Wood
‎2018-09-06 02:54 PM
  • TAC BCX/I2/b3 Controllers
  • Continuum SmartSensor
Example: This information was for units stored in Antarctica with no heat.
All i2/b3 with and without LCD: -30°C to 80°C (-22°F to 176°F)
BCX: Less than 30 days @ -40°C to 65°C (-40°F to 149°F)
The specification for the BCX battery indicates a recommended minimum temperature of 20°C when the battery is discharging, with no time limitation.
The battery could be potentially be stored at -20°C for longer than 30 days with no problems.
As a side note, the minimum charging temperature is 0°C, so be careful to let the units warm up before applying power to the BCX to avoid battery damage.
Continuum SmartSensor: -20°C to 65°C (-4°F to 149°F)
Tags (5)
  • 2787
  • celcius
  • degrees
  • fahrenheit
  • maximum