SpaceLogic Sensor SXWS HMI references

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SpaceLogic Sensor SXWS HMI references
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2242 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SpaceLogic Sensor SXWS HMI references

Janeway Jonas_Brissman Janeway
‎2022-02-10 04:21 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-09-05 07:35 AM

Issue

A large room has multiple SpaceLogic Sensors SXWS (formerly SmartX sensor) and the temperature setpoint is changed in one of them. Is it possible for the temperature setpoint to be changed in the other sensors? 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation SpaceLogic Sensor
  • Building Operation Room Controller (RPC)
  • Building Operation RP-V VAV

Cause

In EBO (EcoStruxure Building Operation) version 3.1 a functionality called HMI references is introduced which can be used in this case. This new functionality makes it possible to have bi-directional bindings for the following value types in the RP series controller

  • Blind position: analog value
  • Occupancy override: digital value
  • Fan speed: multistate value
  • HVAC mode: multistate value
  • Light level: analog value
  • Selected scene: analog value
  • Blind slat angle: analog value
  • Temperature setpoint: analog value

Resolution

This is done by creating a value of the value types supporting the HMI reference functionality in the Application folder of the RP IP controller which the SpaceLogic Sensors are connected to. Then bind that value to the Display properties of each SpaceLogic Sensor

 

Picture1.png

 

 

For example an Analog value is created in the Application folder of the RP-C and then bound to the Display Temperature Setpoint property of each connected SpaceLogic sensor. If then changing the Temperature setpoint from the RP-C that will be distributed to all SpaceLogic Sensors. But also if changing the Temperature setpoint in any of the SpaceLogic Sensors that value will be distributed to the other SpaceLogic Sensors and the RP-C.

 

To see an example on how this can be done please see video:

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • JonasBrissman22
  • MahmoudSayed24
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore