Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SpaceLogic BACnet/IP devices firmware compatibility with EBO and Tridium Niagara N4

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SpaceLogic BACnet/IP devices firmware compatibility with EBO and Tridium Niagara N4
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • PeterEdvik
    PeterEdvik
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
9951 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SpaceLogic BACnet/IP devices firmware compatibility with EBO and Tridium Niagara N4

Mahmoud_Sayed Champion
‎2021-09-28 11:35 AM

Last Updated: RandyDavis Champion ‎2025-09-10 06:33 AM

Issue

What is the compatible SpaceLogic BACnet/IP device firmware version for my EBO or Tridium Niagara N4 installation?

Product Line

EcoStruxure Building Operation, TAC IA Series

Environment

  • SpaceLogic BACnet/IP devices
  • Tridium Niagara N4.10 and later versions Jace 8000/9000
  • Tridium Niagara N4.10 and later versions Enterprise Server 

Cause

The SpaceLogic (formerly known as SmartX) IP Controllers shipped from the factory may not have the latest firmware installed. It is essential to verify that the controller has the latest firmware build loaded for the EcoStruxure Building Operation version or Tridium Niagara N4 build being used before programming the controller.

Resolution

The below table contains the supported SpaceLogic BACnet/IP devices firmware for each EBO release. 

V7.00.0x compatibility.jpg
* CPs are available on: EBO Hotfix List
Note: Versions not mentioned in the table above are out of full support. Refer to earlier versions' release notes for the older versions' compatibility matrix, refer to EBO- Release Notes and Software Support Policy for EcoStruxure™ Building Operation  

Note: RP-C is only supported on EBO 3.0 and later

SpaceLogic/EasyLogic versions compatibility

MP-C-MP-V compatibility.jpg

SpaceLogic BACnet/IP devices can be upgraded using WorkStation, as explained in Updating Firmware in BACnet/IP Controllers. 

SpaceLogic BACnet/IP devices firmware can also be upgraded using the eCommission SmartX Controller mobile application, you can download firmware to either a single BACnet/IP controller or multiple controllers, even if not hosted. This is only supported over an IP connection, as explained in Using the eCommission SmartX Controller Mobile Application to Download Firmware to BACnet/IP Control...

 

Tridium Niagara N4 Compatibility

Note: Previous to Version 1.0, SpaceLogic BACnet/IP devices firmware is only approved at v3.02.03 for Jace 8000 and Niagara Enterprise Server using N4.10 and newer platforms.

Starting in Version 2.0 (Build 77) firmware v4.00.04.02002 CP1 is approved for use.  Make sure and reference the controller type in the table above as well. Release Notes 

Starting with Version 3.1 (Build 85), firmware 6.00.03.03007 CP2 and 7.x RC can be employed. The EasyLogic controllers are supported by the Niagara modules with these releases.  N4.10, 4.13, 4.14 and 4.15 are the only versions with these modules. Product Announcement  

 

 
Labels (2)
Labels:
  • Automated Engineering Tool
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • MahmoudSayed21
  • MahmoudSayed22
  • MahmoudSayed23
  • MahmoudSayed24
  • MahmoudSayed25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore