Error message when starting SigmaX, says "Failed to Create Object", once accepted SigmaX works correctly.
Satchwell Sigma
  • Sigma
  • SigmaX
  • Tools
  • Utilities
Sigma Graphics has not correctly registered in the system registry.
This issue is rectified as detailed below.
1 - Close SigmaX if running.
2 - Start the Sigma server and client.
3 - Open the Sigma graphics editor, and either open an existing graphic, or start a new one.
4 - Modify the graphic and then save the changes.
5 - Shutdown the Sigma client and server, Start SigmaX and confirm its operation.