Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Sigma - Upgrading existing 4.05 / 4.05 SEB sites to Sigma 4.06.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Upgrading existing 4.05 / 4.05 SEB sites to Sigma 4.06.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1660 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Upgrading existing 4.05 / 4.05 SEB sites to Sigma 4.06.

Picard Product_Support
‎2018-09-10 08:21 PM

Issue

Upgrading 4.05 sites to Sigma 4.06

Environment

Upgrade

4.05

SEB

Cause

Overview on upgrading Sigma 4.05 versions to Sigma 4.06

Resolution

General Overview of the upgrade process.

This overview is for background information only; ensure that, when upgrading, the instructions in sections 6.2.4 to 6.2.8 of the release note are followed.

This release provides upgrade utilities which, when run, detect the release at which configuration data was created and selectively convert it as required.

The main utilities are:

  • SgiConvert: Converts .SGI graphics and associated files to the original version of the .SWC format.
  • SigUpgrade: Converts all data (including graphical and tolerances) to the current release format. It must be run after graphics have converted from early .DRW (BAS) and .SGI (earlier Sigma) formats. It examines
  • Also available is the Graphics Optimisation Tool which converts BMP files to JPG files and amends file name references in associated graphics. This tool should only be used in specific circumstances. See section 4.4.3. Revised Web Optimisation Tool for details.
  • In addition any old BAS Graphics can be imported using a DrwSwcCnvrt utility.

During the upgrade it is necessary to shutdown all clients of the server. The point at which this is done must be chosen to suit site circumstances and to minimise downtime.

When Releases 4.00 and later is uninstalled, all data files are left intact (unlike earlier releases).

The Standard Client software release and the Web ActiveX Client software release must both match the release of the server software. Do not allow clients and servers at different releases to attempt connection during the upgrade process. This applies for both Standard Clients and Web ActiveX Clients.

If Remote Alarm Manager is used to read alarm data from Sigma, Remote Alarm Manager 2.0 must be used.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7732
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of