Sigma – UNC Controller Log Data Handling During Server Communication Failure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma – UNC Controller Log Data Handling During Server Communication Failure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1357 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma – UNC Controller Log Data Handling During Server Communication Failure

Picard Product_Support
‎2018-09-06 12:14 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-12 09:11 PM

Issue

This article explains how a Sigma UNC controller manages log data when communication with the server is interrupted.

Product Line

Satchwell BAS & Sigma

Environment

  • Satchwell Sigma - All versions
  • UNC Controllers (V53 and ARM7 Series)

Cause

During normal operation, Sigma controllers log data and periodically upload it to the logging database. These uploads are managed by the UNC controller. If communication with the server fails, the controller temporarily stores the data in RAM until the connection is restored.

Resolution

When communication to the server is lost, the UNC controller follows a structured process to manage log data:

  1. Alarm Buffer Initialization
    • After all files are downloaded, the Alarm Buffer is created.
    • It queues alarms and logs destined for the server.
    • Capacity: Up to 500 entries.
  2. Logging Buffer Allocation
    • Memory is allocated to the Logging Buffer, which stores partially completed log data.
    • V53 Series Controllers (532, 496/596, IC1):
      Allocated 75% of remaining memory.
    • ARM7 Series Controllers (632, 696/796, IC3):
      Allocated 512 kB.
  3. Logging Track Structure
    • The Logging Buffer uses 138-byte Tracks, with one Track per logged object.
    • Log records are added to the Track as events occur.
    • Once full, the Track is transferred to the Alarm Buffer.
  4. Records per Track by Object Type
    Log Type Object Type Records per Track
    Timed Analogue 25
    Timed Digital 100
    Event Analogue 14
    Event Digital 32
    Alarm/Report (Log) Any 28
  5. Manual Log Retrieval
    • Partially full Tracks can be manually transferred to the Alarm Buffer via:
      Diagnostics > Options > Retrieve Logs
  6. Autodial Connection Behavior
    • If an Autodial connection is configured, a call is initiated when:
      • Any non-opportunistic alarm or log is placed in the Alarm Buffer.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 8131
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore