Sigma - The IC3-SNP Integration Controller does not display negative values correctly.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - The IC3-SNP Integration Controller does not display negative values correctly.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1049 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - The IC3-SNP Integration Controller does not display negative values correctly.

Picard Product_Support
‎2018-09-06 02:04 PM

Issue

Negative values presented to an IC3-SNP Integration Controller are displayed starting at 65535.

Environment

Sigma

Integration Controllers

IAC Controllers

Unifact Controllers

Cause

The IC3-SNP Integration Controller calculates the negative value incorrectly.

Resolution

To overcome this issue it will be necessary to create a new Lookup table and to allocate it to the IC3-SNP Analogue Input object.

1 - In Sigma "System Manager" select "System Setup" and create a new lookup table, using the configuration shown below.

2 - Edit the Analogue Input object to include the new Lookup Table number, select to download the object.

3 - In Sigma "System Diagnostics" download the Lookup Table to the IC3-SNP.

4 - The lookup table shown above assumes that the value being presented is in whole numbers, i.e. a received value of 1 equals 1, but there are instances when the value received may have a *10 factor applied. In this case the lookup table is modified as shown below.

Input         Output
0               0
32767       3276.7
32768      -3276.8
65535      -0.1

Labels (2)
Labels:
  • Field Devices
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 4721
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of