Sigma – Site Requirement to Control Five Chillers in Sequence

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma – Site Requirement to Control Five Chillers in Sequence
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1675 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma – Site Requirement to Control Five Chillers in Sequence

Picard Product_Support
‎2018-09-06 01:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 03:54 AM

Issue

Assistance is required to create a Sigma program that controls five chillers in a fixed sequence. The existing attempt does not function as intended.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell BAS & Sigma

Cause

  • Control five chillers in a fixed sequence
  • Introduce a configurable delay (default: 20 minutes) between starting each chiller
  • Allow for an adjustable temperature differential to determine when chillers are activated

Resolution

The following program logic can be used:

Program Logic

10  XFlo = POINT 0|144 - POINT 0|140
20  IF XFlo <= 0.000000 THEN XFlo = 0.000000
30  IF XFlo >= POINT 0|141 THEN XFlo = POINT 0|141
40  XFlo = (XFlo / POINT 0|141) * 100.000
50  XInt = 0
60  IF XFlo >= 20.0000 THEN XInt = XInt + 1
70  IF XFlo >= 40.0000 AND YInt >= 1 THEN XInt = XInt + 1
80  IF XFlo >= 60.0000 AND YInt >= 2 THEN XInt = XInt + 1
90  IF XFlo >= 80.0000 AND YInt >= 3 THEN XInt = XInt + 1
100 IF XFlo >= 100.000 AND YInt >= 4 THEN XInt = XInt + 1
110 IF TIME LEFT THEN GOTO 180
120 IF XInt > YInt THEN GOTO 150
130 YInt = XInt
140 GOTO 190
150 ZInt = INT(POINT 0|142) * 60.0000
160 SET TIMER ZInt
170 YInt = YInt + 1
180 IF XInt < YInt THEN SET TIMER 0
190 RETURN VIA TEXT 92 VALUE FLOAT(YInt)

Object Descriptions

Object Type Description
140 SPA Object Setpoint (reference temperature)
141 SPA Object Differential (range over which chillers activate)
142 SPA Object Delay time (in minutes)
144 AI Object Chiller return temperature

Chiller Command Configuration

Each chiller command object must use hysteresis control. Configure as follows:

Chiller Low Setting High Setting
1 0.1 0.9
2 1.1 1.9
3 2.1 2.9
4 3.1 3.9
5 4.1 4.9

Additional Notes

  • Ensure the programmable object is linked to the chiller command objects.
  • The hysteresis settings prevent rapid cycling and ensure stable operation.

For a copy of the above text, click here.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (2)
  • Find more articles tagged with:
  • 6213
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore