Sigma - Short Text Not Displaying Correctly

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Short Text Not Displaying Correctly
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1047 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Short Text Not Displaying Correctly

Picard Product_Support
‎2018-09-06 12:37 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-21 10:17 PM

Issue

Short Text entries in Sigma Version 4 display correctly on the local client, but not on remote clients.

Product Line

Satchwell BAS & Sigma

Environment

Sigma Version 4.0

Cause

Sigma stores Short Text files based on the regional settings of the PC. The file path is typically:

C:/Sigma/Data/Locality/English United_Kingdom (if UK)

If the Sigma Server and Sigma Client have different regional settings, Short Text entries added on one may not appear correctly on the other.

Example:

  • Server locale: UK
  • Remote client locale: US

→ The remote client will look for Short Text in the US folder, which may not contain the new entries added on the UK server, resulting in incorrect object display.

Resolution

Ensure consistent regional settings across all Sigma machines:

For Windows XP / Server 2003:

  1. Go to Control Panel > Regional and Language Options
  2. Tab 1 (Regional Options):
    • Set Standards and Formats and Location to the correct region.
  3. Tab 3 (Advanced):
    • Set Language for non-Unicode programs to the correct region.

For Windows 7 / Server 2008:

  1. Go to Control Panel > Region and Language
  2. Tab 1 (Formats):
    • Set Format to the correct region.
  3. Tab 2 (Location):
    • Confirm Location is correct.
  4. Tab 4 (Administrative):
    • Set Language for non-Unicode programs to the correct region.

Summary

To ensure Short Text displays correctly across all Sigma clients:

  • Align regional settings on all Sigma PCs.
  • This prevents mismatches in folder paths and ensures consistent object display.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 7421
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore