Sigma LON Card is Applicationless and Cannot Be Reset by IC3 LON Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma LON Card is Applicationless and Cannot Be Reset by IC3 LON Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2239 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma LON Card is Applicationless and Cannot Be Reset by IC3 LON Controller

Picard Product_Support
‎2018-09-09 10:28 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 09:47 PM

Issue

Cannot commission an IC3 LON controller in LonMaker. It has become applicationless and the red service LED is flashing or permanently lit.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell Sigma IC-LON/IC3-LON

Cause

The Echelon chip may become 'locked' due to:

  • Corrupted controller files
  • Excessive LON network traffic (>50% bandwidth)
  • Cold start or startup mode triggering a reset

Resolution

Although hardware replacement is no longer an option due to the discontinuation of the S-LON plug-in card, the following recovery steps may help restore controller functionality:

For Flashing Red LED

  1. Download a clean set of controller files to the IC3 controller.
  2. Launch NodeUtil.exe on a laptop with an FTT-10 Echelon adapter.
  3. Connect the LON cable to the controller.
  4. Press the onboard reset button on the controller.
  5. Activate the service pin on the LON card; the Neuron ID should appear in NodeUtil.
  6. In NodeUtil, select R to reboot the 3150 node and enter the Node ID.
  7. Confirm the reset when prompted.
  8. The service LED should stop flashing, indicating the controller is no longer applicationless.

⚠️ Note: If repeated resets and service pin activations fail to generate a response, and hardware replacement is not an option, the controller may no longer be recoverable. Consider isolating the device and consulting with technical support for further guidance.


For Permanently Lit Red LED

  1. Download clean controller files.
  2. Repeat the NodeUtil reset procedure as above.
  3. If the Echelon chip locks again, repeat the reset process.

Alternative Recovery Procedure (Customer-Provided)

If the standard reset does not resolve the issue, the following steps have been reported to help:

  1. Disconnect the IC LON from both the LON and Sigma networks.
  2. Use the SCDU tool to re-node the IC LON to a temporary IP address.
  3. Power off the IC LON and remove the LON daughterboard.
  4. Power on the mainboard without the daughterboard, then reinstall the daughterboard.
  5. Reconnect using NodeUtil and clear the LON communication buffers.
  6. Verify that the red service LED is off and the green LON heartbeat LED is active.
  7. Re-node the IC LON to its original IP and verify operation.

Important Notice

The Sigma IC-LON plug-in card (S-LON) has been discontinued as of 29 December 2017 and is no longer available for replacement. All troubleshooting must be performed using existing hardware.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
NODEUTIL.zip
Osn117.zip
Tags (14)
  • Find more articles tagged with:
  • 5287
  • add
  • CraigEllis25
  • exit
  • find
  • GaryMontague19
  • go
  • help
  • output
  • RyanSuar19
  • status
  • transceiver
  • verbose
  • wink
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore