Sigma Integration Controllers - Hardware Alarms - How can these alarms be disabled?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Integration Controllers - Hardware Alarms - How can these alarms be disabled?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1296 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Integration Controllers - Hardware Alarms - How can these alarms be disabled?

Picard Product_Support
‎2018-09-06 09:38 AM

Issue

How can Sigma IC Hardware Alarms be disabled?

Environment

Sigma

IC

Integration Controllers

Hardware Alarms

Cause

Large numbers of alarms were caused after a power fail.

Resolution

Hardware alarms are generally a good thing as they advise of a problem on the system, but should it be necessary to disable them, then this is achieved by modifying the Gateway.txt file.

There are a range of Sigma IC's available and there are differences between them, so to ensure the correct changes are made, the appropriate IC documentation should be reviewed.

In this example the Gateway.txt of an IC-Modbus will be examined.

Each object entry in the Gateway.txt can consist of up to nine fields as follows - 55,1,3,101,1,2,0,0,0, and it is the ninth field that controls the Hardware Alarm Suppression.

If the ninth field is not used or is set to zero, then the hardware alarms will operate as normal, but if the ninth field is set to 1, then these alarms are disabled.

Below shows a section of the Modbus Gateway.txt, where the object field entries are defined.

; Format of list, 8 or optionally 9 parameters per entry:-
; 1   Sigma Object Number,
; 2   Controller Address - Hiromatic Unit not units on sublan
; 3   Modbus Command ( 3, 4, 16, 144)
;      Crompton meters IC uses functions listed (serial only, not TCP)
;      3   Read Holding register (AI)
;      4   Read Input registers (AI)
;      16  Preset multiple registers (AO)
;      144  Set MSB - Write Demand time (DO)
; Note :- Resetting the Demand Period for the CROMPTON is a special case.
; The most significant bit must be set, i.e. Function = 144, and a DO Object
; must be used. This ensures that the Demand Period is only reset
; when the DO Object switches from 'OFF' to 'ON'
; 4  Register Address
; Use the formula
; Register Address = Address-1. E.G. for return temp, at address 233
; enter the value 232.
; 5  Min time in seconds before polling same controller (Default 1 second)
; 6  Number of consecutive objects to read (inputs objects only, 0 for outputs)
;    Maximum 7 objects
;    Special case: 32- bit data Input objects may be read in a single
;                  transaction
;    Note: This is applicable to Function Codes 0x03 and 0x04 only.
;    Format: 0xST02
; where-
;    S = Swapped? (0 - unswapped; 1 - swapped)
;    T = data type (0 - 16 bit; 1 - unsigned 32 bit; 2 - signed 32 bit;
;                   3 - float 32 bit)
;
; 7  Min Value (output objects only, 0 for inputs)
; 8  Max Value (output objects only, 0 for inputs)
; 9  Hardware Alarm Message Suppression Flag (optional),
;   0 = Don't suppress,   1 = Suppress

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 15905
  • harware
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of