Sigma IC & BAS PIU Error Messages

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma IC & BAS PIU Error Messages
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2031 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma IC & BAS PIU Error Messages

Picard Product_Support
‎2018-09-09 05:18 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-05 08:20 PM

Issue

When using a BAS terminal connected to a PIU (Protocol Interface Unit), users may encounter unexplained system messages such as:

“Message No. 19920 not available. Please contact Product Support.”

These messages indicate that the terminal received a system message from the PIU that is not defined in the local Messages.ini file.

Product Line

Satchwell BAS & Sigma

Environment

BAS PIU and Sigma Pre-release 4 System Messages

Cause

The Messages.ini file used by the BAS terminal has a maximum size limit of 64KB. Due to this constraint, not all possible PIU error messages are included by default. As a result, some messages—especially those from less commonly used subsystems—may be missing.

Message Number Ranges by Subsystem

Below is a breakdown of message number ranges associated with various subsystems:

Subsystem Message Range
BAS 1 – 10499
SNP Gateway 10500 – 10999
CHUBB Remote Access 11000 – 11499
CEGELEC 11500 – 11999
OTIS 12000 – 12499
CCURE 12500 – 12999
WORMALD 13000 – 13499
ASIC 13500 – 13999
SIMPLEX 14000 – 14499
CARRIER DATAPORT 14500 – 14999
EXPRESS LIFT 15000 – 15499
CARDKEY 15500 – 15999
Mitsubishi 16000 – 16499
Liebert 16500 – 16999
IMPACC 17000 – 17499
YORK 18000 – 18499
AUTOFLAME 19000 – 19100
AUTOMETERS 19100 – 19199
MITSUBISHI PLC 19200 – 19299
SIEBE MICRONET 19400 – 19499
CROWCON 19500 – 19599
MNI (MicroNet Interface) 19700 – 19799
Colt OPV 19800 – 19899

Resolution

To resolve missing message errors:

  1. Obtain the full message list:

    • A more complete set of BAS error messages is available in the messages.doc attachment.
  2. Update the Messages.ini file:

    • Copy the relevant section from the full message list.
    • Paste it into the C:\Bas\Data\Messages.ini file.
    • Ensure messages are inserted in correct numerical sequence.
  3. File Size Limitation:

    • The updated Messages.ini file must not exceed 64KB. If necessary, prioritize messages relevant to your system configuration.

Example

If your system uses MODBUS and you encounter message 19920, locate the MODBUS section in the full message list and add it to your Messages.ini file.

example.PNG

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (3)
  • Find more articles tagged with:
  • 5182
  • CraigEllis25
  • DavidChild19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore