Sigma IC-LON: SNVTs Not Updating Due to Incorrect Connection Type
  • Sigma IC-LON: SNVTs Not Updating Due to Incorrect Connection Type
  • CraigEl
    CraigEl
‎2018-09-10 10:56 AM
Last Updated: Administrator CraigEl Administrator ‎2025-11-04 11:15 PM
Some SNVTs (Standard Network Variable Types) are not updating correctly within the Sigma IC-LON.
Satchwell BAS & Sigma
Satchwell Sigma IC-LON / IC3-LON
The issue arises when LON bindings are not configured using the correct “Sigma” connection type. If the IC-LON Plug-in does not create or apply this connection type properly, SNVT updates may fail or behave inconsistently.
  • Review the IC-LON Configuration Document
    • Refer to the attached document: 01.08.22-4_PIB ICLON Configuration.pdf
    • This guide includes detailed steps for setting up the IC-LON Plug-in and selecting the correct connection type.
  • Ensure “Sigma” Connection Type is Used
    • The IC-LON Plug-in must create a connection type labeled “Sigma”.
    • The Service Type should be set to “Unackd”  and "Use Broadcast" set to Yes in the advanced settings.
  • Verify Bindings
    • Confirm that all SNVT bindings use the correct connection type.
    • Incorrect types will prevent proper communication and updates.
  • Satchwell BAS & Sigma
Tags (2)
  • 7538
  • CraigEllis25