Sigma - How does the alarm archiving at release 4.5 SEB work?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - How does the alarm archiving at release 4.5 SEB work?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
940 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - How does the alarm archiving at release 4.5 SEB work?

Picard Product_Support
‎2018-09-06 01:12 PM

Issue

Alarm archiving at release 4.5 SEB.

Environment

Sigma

Alarms

Archiving

AlarmLog.rec

Cause

The alarm archiving mechanism is unclear.

Resolution

Sigma 4.05 SEB includes a mechanism for archiving alarms on basis of a number of conditions.

User Settings.

The user is able to set the following "Alarm File Sizes".

  •  Current (Max). this is the maximum number of alarm records * 1000.
  • Archive (20 - 50) %. this is the percentage of the "Current (Max)" record setting that will be archived. 

These setting are located in the "System Setup" / "General" / "Archive Sizes" as shown below.

Automatic Alarm Archiving.

The Sigma alarm archiving process is an automatic function that will operate to the requirements of the settings above.

When an archive takes place a low level alarm message is produced to advise the user, it does not require acknowledgement as it is only for information.

Archive alarm files are stored in the C:\Sigma\Data\ArchivedAlarms folder using a sequence reference number.

Timed Alarm Archiving.

These Schedules are located in the "System Setup" / "General" / "Scheduled Actions", and the first step is to create an "Action", as shown below.

 Next create either a "Daily" or a "Once Only" schedule.

The alarms will now be archived on a regular basis as dictated by the above schedule.

Please note that the archive will still follow the configuration setup up in "Archive Sizes".

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 6433
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of