Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Sigma Graphics - A local Sigma client does not display the background image of a Graphic, but a remote Sigma client does.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Graphics - A local Sigma client does not display the background image of a Graphic, but a remote Sigma client does.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1174 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Graphics - A local Sigma client does not display the background image of a Graphic, but a remote Sigma client does.

Picard Product_Support
‎2018-09-06 12:20 PM

Issue

A local Sigma client does not display the background image of a Graphic, but a remote Sigma client does.

Environment

Local client

Remote client

Background

Graphic

Cause

If a large image (bmp or jpg) has been used as the background in a Sigma graphic, the local client does not display the picture, but a remote clients or web clients do.

Resolution

Some older machines, because of their graphics capabilities cannot display some Sigma graphics. Netbooks or laptops may also have a similar issue.

Users may also experience poor performance when opening graphics, animations and editing graphics.

In a lot of cases it will be possible to purchase a graphics adapter card that can display these graphics, but where this is not the case the size of the graphics files will need to be reduced in order to display the graphics correctly.

The recommended replacement Graphics adapter is as follows; 

1GB graphics adapter which supports the appropriate version of DirectX (DirectX 11 for Windows 7 family).

It should be noted that it will not always be possible to buy a graphics adapter that will be compatible with the specific machine that has the problem. In this case the PC should be replaced with a better specification machine. 

To summarise..

  • Servers and Netbook computers will not be supported for Sigma Clients.
  • A suitable graphics card will be required as specified above to display Sigma Graphics.
  • Users may need to reduce the size of the graphics files where a suitable graphics card cannot be installed.
  • Most modern workstation computers will be capable of displaying Sigma graphics.
  • Most server machines will not be capable of displaying sigma graphics.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 7967
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of