Sigma - Globals do not work when an IP Address structure of 192.168.xxx.xxx Mask 255.255.0.0 is used.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Globals do not work when an IP Address structure of 192.168.xxx.xxx Mask 255.255.0.0 is used.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1073 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Globals do not work when an IP Address structure of 192.168.xxx.xxx Mask 255.255.0.0 is used.

Picard Product_Support
‎2018-09-06 12:39 PM

Issue

Sigma globals do not work.

Environment

Sigma

Globals

Mask 255.255.0.0

Classful

Classless

Cause

The site is using a class C address, with a class B subnet mask.

Resolution

The following is an explanation of why the Sigma globals in this configuration do not work.

An IP Address is divided in to two sections: Net ID and Host ID. The Host ID is further divided in to two Sections: Subnet ID and Host ID.

  • The Subnet Mask determines the Subnet ID bits and Host ID bits.
  • Number of Mask bits should be greater than that of Net ID bits.

For example a Sigma address is 192.168.0.1 with 24 bit mask 255.255.255.0

  • Number of subnet ID bits is zero and Host ID bits is 8;
  • Broadcast address is 192.168.0.255

 With 28 bit mask 255.255.255.240

  • Number of subnet ID bits is 4 and Host ID bits is 4;
  • Broadcast address is 192.168.0.15

 For Class C:

  • Address range is: 192.0.0.0 to 223.255.255.255 inclusive
  • Net ID is 24 bits; Host id is 8 bits; Minimum Mask size is 24 bits;

 For Class B:

  • Address range is: 128.0.0.0 to 191.255.255.255 inclusive
  • Net ID is 16 bits; Host id is 16 bits; Minimum Mask size is 16 bits;

In the site set up, 192.168.xxx.xxx is a Class C address; this can have at least 24 bit mask; 16 bit mask is invalid;

Using an Address 190.168.xxx.xxx works correctly because it is a Class B address and supports 16 bit masking; hence works properly.

For globals to work correctly, either use >= 24 bit mask for the subnet 192.168.xxx.xxx, or move to class B subnet 190.168.xxx.xxx.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 7354
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of