Sigma - Creating a Programmable object to identify if a temperature is higher or lower than an earlier one.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Creating a Programmable object to identify if a temperature is higher or lower than an earlier one.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
960 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Creating a Programmable object to identify if a temperature is higher or lower than an earlier one.

Picard Product_Support
‎2018-09-06 01:09 PM

Issue

The requirement is to save a temperature taken at 10:00am, and to compare it with the temperature taken at 4:00pm. If the temperature was found to be lower at 4pm, then the output of the programmable object will be false, if the temperature is found to be higher, then the output will be true.

Environment

Sigma

Programmable Object

Program

Prog Point

Cause

Assistance is required to create a suitable programmable object.

Resolution

The following programme will meet the requirements.

10 IF TIME = 10:00 THEN XINT = 1

20 IF TIME = 16:00 THEN XINT = 2

30 IF XINT UP THEN GOTO 50

40 GOTO 100

50 IF XINT = 1 THEN XFLO = POINT 1

60 IF XINT = 2 THEN YFLO = POINT 2

70 IF XINT <> 2 THEN GOTO 90

80 IF XFO > FLO THEN YINT = 1 ELSE YINT = 0

90 XINT = 0

100 IF YINT = 1 THEN RETURN TRUE "Higher" ELSE RETURN FALSE "Lower"

Lines 10 and 20 establish if this is the first or second entry.

Line 30 establishes that XINT has increased.

Lines 50 and 60 store the two temperature values.

Line 70 decides if the comparison should be made.

Line 80 decides if the 4pm temperature is higher or lower than the 10am value.
 

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 6442
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of